关于巴鲁夫直线位移传感器SSI信号带B和不带B的区别,高手帮忙解答一下

[复制链接]
  • 打卡等级:偶尔看看
  • 打卡总天数:94
  • 打卡总奖励:261
发表于 2016-3-30 16:41:30 | 显示全部楼层 |阅读模式
巴鲁夫直线位移传感器SSI接口的选型中有带B的,说明是用于同步控制的,见附件。
但是我有个疑问,从SSI通信的原理来说,数据的读取是靠控制器发的时钟信号来进行传输的。
也就是说无论在什么情况下,什么时候传数据取决于控制器,而不取决于传感器。
为什么传感器加B以后,就更适用同步控制了呢?百思不得其解,还望高手解答

BTL5

BTL5
  • 打卡等级:偶尔看看
  • 打卡总天数:101
  • 打卡总奖励:315
发表于 2016-3-31 02:21:29 | 显示全部楼层
这是一个很好的问题!
始终使用B(同步)SSI棒的运动控制。
与异步SSI棒,运动控制器不能计算速度或加速度

我需要更详细的解释翻译的帮助

This is a very good question!
Always use the B ( synchronous ) SSI rod for motion control.
With asynchronous SSI rods, the motion controller can not calculate velocity or acceleration
回复 支持 反对

使用道具 举报

  • 打卡等级:偶尔看看
  • 打卡总天数:94
  • 打卡总奖励:261
 楼主| 发表于 2016-3-31 07:58:47 | 显示全部楼层
PEN 发表于 2016-3-31 02:21
这是一个很好的问题!
始终使用B(同步)SSI棒的运动控制。
与异步SSI棒,运动控制器不能计算速度或加速 ...

You can explain it in english
Some translation software translation is not accurate
回复 支持 反对

使用道具 举报

  • 打卡等级:偶尔看看
  • 打卡总天数:94
  • 打卡总奖励:261
 楼主| 发表于 2016-3-31 08:03:47 | 显示全部楼层
You can explain it in english
Some translation software translation is not accurate
回复 支持 反对

使用道具 举报

  • 打卡等级:无名新人
  • 打卡总天数:15
  • 打卡总奖励:59
发表于 2016-3-31 17:19:34 | 显示全部楼层
看来是讯号是否实时还是容许滞後。
若是闭环控制,必需实时。比例控制则可考虑异步产品。
回复 支持 反对

使用道具 举报

  • 打卡等级:偶尔看看
  • 打卡总天数:101
  • 打卡总奖励:315
发表于 2016-4-1 03:57:25 | 显示全部楼层
mars_haha 发表于 2016-3-31 07:58
You can explain it in english
Some translation software translation is not accurate

Hydraulic systems are like a mass between springs.   The mass is the piston and connected load.   The two springs are the volumes of oil between the piston and valve on both sides of the piston.   Therefore hydraulic systems tend to act like a second order under damped system.  It is necessary to increase the damping factor electronically to reduce over shoot or oscillation.

For high performance hydraulic motion control the positions must be sampled at consistent time intervals and the motion controller must know exactly when these time samples are taken.   Sampling at consistent time intervals allow the motion controller to compute accurate velocities and accelerations of the actuator.   When accurate velocities and accelerations are known then it is possible to use the derivative and second derivative gain for closed loop control.   The derivative and second derivative gain provide damping that reduce or eliminate oscillations.  The derivative and second derivative gains are necessary when controlling systems with heavy loads and low natural frequency.
When positions are sampled asynchronously the motion controller does not know the time between two positions.  Therefore it can’t calculate velocity by using
Velocity(n)=(Position(n)-Position(n-1))/(Time(n)-Time(n-1).    The RMC motion controllers can calculate acceleration if the MDT ( Magnetostrictive Displacement Transducer ) rod samples are consistent increments.   Then
Acceleration(n)=(Position(n)-2*Position(n-1)+Position(n-2))/Δt^2.  If Δt is not known then the calculated acceleration will not be accurate.

MDT determine position by sending an electric pulse down a wave guide in the middle of the rod.   A start pulse is returned that starts a high speed counter/timer.  When the electric pulse meets the magnetic field of a magnet mounted on the back of the piston it interaction causes the wave guide to twist.  The twisting motion takes time to get back to the twist detector in where the electronics are.  A stop pulse is generated that stops the high/speed timer counter.  The transmitter and twist detector are in the small case at the end of the rod. The time between when the pulse is sent down the rod ( the start pulse ) and the time the twist is detected ( the stop pulse ) determines how far the magnet on the back of the piston is away from the transmitter.   What is important is that the pulse goes down the rod at almost the speed of light.  The time the twist takes to get back from the magnet to the twist detector is what is measured.    What is important is that the positon that is measure is the position at the time the pulse is sent down the rod.   Therefore these pulses must be generated at constant time intervals to get positions at constant time intervals.

So what constant time interval should be used?   The RMC motion controllers can be set to update every 250 micro seconds.   If the MDT rod updates every 1 millisecond then the motion controller will see the same position 3 times in a row and then a big change on the fourth sample.   This is unacceptable.   It defeats the purpose of controller closing the loop every 250 microseconds.  The MDT rod must provide positions to the motion controller when the motion controller asks for position and the pulses must be sent down at the same rate and time as the motion controller ask for them so that the positions are always synchronous the motion controllers closed loop update rate.

The need for synchronous positions was made clear to me in 1990 when I was at a trade show.  I talked to the head of engineering at Balluff in the US.   Back then there wasn’t SSI and the ability to count the time between the start pulse and stop pulse with precision didn’t exist or was just becoming available.  
About 20 years ago Temposonics introduced the first SSI rods at a trade show.   There was a lot of pressure for Delta to support the new SSI rods but we resisted because the new SSI rods would not sample synchronously with the motion controller.   We could not see the advantage of being able to get back a position with a resolution of 10 microns unless the actuator was stopped.   When moving at 1 meter per second the actuator move 1 millimeter per millisecond.  The motion controller did not know when within the 1 millisecond period the 10 micron position was valid so it was impossible to compute accurate velocities.  The simple method of counting the time between start and stop pulses provided less resolution but was actually more accurate when moving because the motion controller had control of when the start pulse was generated.   About 2 years of heated discussion occurred before Temposonics decided to make their SSI rods synchronous.  I am pretty sure that all the Temposonics rod meant for motion control are synchronous since the late 1990s.   Since then we have had no problem with customers buying asynchronous SSI rods.

Balluff  provided Delta with several SSI rods for testing.  The first ones were asynchronous.  Some could only update position every 2 millisecond.  Later Balluff caught up with Temposonics.  What bothers me is that Balluff still sells asynchronous SSI rods.   If the customer should buy an asynchronous SSI  and use it with our controller the results will not be good.  Using proportional only control is not good for reason I have stated in previous threads.

This is how we test MDT rods.
http://v.youku.com/v_show/id_XMTI2NDk4OTc0OA==.html
Notice that the velocity is smooth.

Delta makes over 50%, a Rockwell marketing persons said over 80%,  of the industrial hydraulic motion controllers used in the US and Canada.   Delta makes the 1746-QS,  1756-HYD02 and 1756-M02AS that Rockwell ( Allen Bradley ) sells as their product.  Both Balluff and Temposonic cooperate with Delta because the MDT rods must work with the hydraulic motion controllers used in the US and Canada.  We have the means to test valves and MDT rods.
We get new MDT rods to test for compatibility before they are sold to the public.
回复 支持 反对

使用道具 举报

  • 打卡等级:偶尔看看
  • 打卡总天数:94
  • 打卡总奖励:261
 楼主| 发表于 2016-4-6 09:52:09 | 显示全部楼层
PEN 发表于 2016-4-1 03:57
Hydraulic systems are like a mass between springs.   The mass is the piston and connected load.    ...

谢谢,基本看明白了。
找了两张图片,能够比较好的说明这个问题。


asynchronous

asynchronous

synchronous

synchronous
回复 支持 反对

使用道具 举报

  • 打卡等级:偶尔看看
  • 打卡总天数:94
  • 打卡总奖励:261
 楼主| 发表于 2016-4-6 09:56:58 | 显示全部楼层
PEN 发表于 2016-4-1 03:57
Hydraulic systems are like a mass between springs.   The mass is the piston and connected load.    ...


Are  the 1746-QS,  1756-HYD02 and 1756-M02AS  delta company?

What‘s capability of 1756-HYD02  With respect to rmc150?
回复 支持 反对

使用道具 举报

  • 打卡等级:偶尔看看
  • 打卡总天数:94
  • 打卡总奖励:261
 楼主| 发表于 2016-4-6 10:00:13 | 显示全部楼层
This is how we test MDT rods.
http://v.youku.com/v_show/id_XMTI2NDk4OTc0OA==.html
Notice that the velocity is smooth.

英语水平不好,不是太明白。如果能够加上中文字幕,就太好了。
回复 支持 反对

使用道具 举报

  • 打卡等级:偶尔看看
  • 打卡总天数:101
  • 打卡总奖励:315
发表于 2016-4-6 11:11:14 | 显示全部楼层
三角洲设计和制造的1996 - 1997年的1746-QS罗克韦尔。罗克韦尔销售1746-QS为他们的产品。
1746-QS项目进展这么好罗克韦尔问三角洲设计HYD02和M02AS。三角洲不能出售这些液压运动控制器除了洛。

我会建议1756-M02AS在HYD02因为M02AS采用更高分辨率的同步SSI反馈。

1746-QS是旧的。不要买expept取代旧1746-QS控制器。

的RMC150更灵活,更有能力,因为它是一个较新的设计。比较需要太长时间。问一些简短的回答具体问题。

看到
http://deltamotion.com/
http://forum.deltamotion.com/

如果没有这个星期的翻译帮助。我必须使用计算机:(

Delta designed and manufactured the 1746-QS for Rockwell in 1996-1997.  Rockwell sells the 1746-QS as their product.
The 1746-QS project went so well Rockwell asked Delta to design the HYD02 and M02AS.  Delta cannot sell these hydraulic motion controllers except to Rockwell.

I would recommend the 1756-M02AS over the HYD02 because the M02AS uses higher resolution synchronous SSI feedback.

The 1746-QS is old.  Don't buy expept to replace old 1746-QS controllers.

The RMC150 is more flexible and more capable because it is a newer design. A comparison would take too long.  Ask specific questions that have short answers.

See
http://deltamotion.com/
http://forum.deltamotion.com/

If have no translation help this week.  I must use the computer :(




回复 支持 反对